D103 in delta with no neutral available.

PATS yesterday at 3:15 p.m. in General questions updated yesterday at 4:15 p.m. 2

I've just received a D103-1000 that I intend to use between a generator and motor, the motor is driven through an inverter. This is connected in delta without a neutral. Can the energy meter be wired into this connection without a neutral wire?

Answered

Hello.

The D103 energy monitor can be used for 3-phase WYE grid with neutral (star) or for 1-phase three-point measurement.

It is not possible to connect the device without a neutral, sorry.

The D103 device is powered from inputs N and L1; internal power supply rated for 90-260 Vac.

Thank you for the quick reply.