How is it possible to create a combined condition for the relay contact at the D103?

I want the relay to close (ON) when Total Power (d.TW) is > than Total Reverse Power (d.TrW) and open (OFF) otherwise

BAD, I'M UNSATISFIED

the answer doesn't help. 

i still don't know how two values can be compared and set as condition for the relay output control.

Satisfaction mark by HR 1 month ago
Answered

You can set the conditions in the device web-settings.

See the CONDITIONS section in the manual.

https://support.smart-maic.com/communities/1/topics/25-gde-mozhno-skachat-instruktsiyu

In your case, you should understand that at one point in time one of the values will be equal to 0.
If [W]>0 then [rW] at this moment is equal to 0.
And if [rW]>0 then [W]=0.
Accordingly, the conditions will be simple.
[W]>0 => RELAY ON
[rW]>0 => RELAY OFF

Below is an example from the device settings.

Image 2141

Thank you very much for your reply.

However,  in my application there is a single phase solar system on one phase connected which causes that Total Power can be > 0 and at the same time Total Reverse Power also >0

Image 2142

Yes, if these are different lines, then maybe.

But such a condition cannot be set in the device settings, sorry.

You can collect data and control the relay via the API.

In this case, it is possible to write a script yourself and control the relay under any conditions.